B bhall1 Member Dec 31, 2007 #1 What is the proper way of terminating VFD drive cable? Can the braided shield be trimmed back with the rest of the outer insulation/jacket.
What is the proper way of terminating VFD drive cable? Can the braided shield be trimmed back with the rest of the outer insulation/jacket.
C cbranter Member Location Provost, Alberta, CANADA Dec 31, 2007 #2 what ty[e of cable are you describing? ESP HV cable has special connectors where it exits the well casing
what ty[e of cable are you describing? ESP HV cable has special connectors where it exits the well casing
B benaround Senior Member Location Arizona Dec 31, 2007 #3 bhall1, The shield is usually grounded at the supply end, manafactures instructions should be followed in any case.
bhall1, The shield is usually grounded at the supply end, manafactures instructions should be followed in any case.
iwire Moderator Staff member Location Massachusetts Jan 1, 2008 #4 I agree with Frank, you bond the shield to ground on the supply end and isolate it at the other end.