I have an engineering spec which says that "VFDs larger than 700 to 2500 KVA shall be powered at 4.16 kV, 3 phase, 3-wire" and
"VFDs 700 KVA or less shall be powered at 480V, 3 phase, 3-wire"
I have a 400 HP cooling tower fan motor ( non-VFD Driven) fed from a medium voltage switchgear. and on the other hand i have a 400 HP ID fan motors (VFD driven) fed from a low voltage switchgear.
Why does inclusion of VFDs in the design allows the ID fan motors to be low voltage. The spec clearly states that motors above 250 HP would be fed from a 4160 switchgear. Any idea..
Thanks
Shailesh
"VFDs 700 KVA or less shall be powered at 480V, 3 phase, 3-wire"
I have a 400 HP cooling tower fan motor ( non-VFD Driven) fed from a medium voltage switchgear. and on the other hand i have a 400 HP ID fan motors (VFD driven) fed from a low voltage switchgear.
Why does inclusion of VFDs in the design allows the ID fan motors to be low voltage. The spec clearly states that motors above 250 HP would be fed from a 4160 switchgear. Any idea..