A quick rundown is that this has occurred twice now on board a ship where a 3Ph 480v 200hp VFD for a refrigeration compressor suffers a catastrophic failure resulting in the entire power system tripping off line. The power plant consists of multiple 480v generators fed into the power distribution panel the failure trips both breakers of the generators currently feeding the distribution panel that are online at the time as well as overloading the generators causing them to completely shut down. From the distribution panel there is another breaker that feeds power to the refrigeration panel and then a third breaker that supplies the VFD power. All of these breakers trip when the failure occurs. My concern is that obviously the breaker in the refrigeration panel for the VFD and the breaker that supplies the are not adequately protecting the rest of the power distribution system. I suspect that the somewhere along the line the distribution is improperly set up/installed and was hoping you could help point me in the right direction. I am sure that there is further information you will need and I will certainly provide it I will just need a nudge in the right direction here and there to properly track this down and correct this system.