I would like to get some input from everyone. We have had two Square D Altivar VFD's blow up on the same motor in a month. Square D hasn't even gotten back to me with any advice or suggestions on where to go from here. My customer ordered a dust system for their train loading system at a grain elevator about two years ago. I ordered my MCC equipment at the same time and it showed up about 6 months later. The mechanical equipment finally showed up last March and we had it running in late April. We had a VFD failure after about 200 hours of run time and of course since it was sitting in packaging for a year and a half there was no arguing warranty replacement. My company has installed maybe a hundred VFD's over the years from 1 hp to 400 hp and I havent ever had to deal with an event like this. The wires for this motor leave the MCC room underground for about 40' through an existing PVC conduit that houses some other smaller 480 volt motors. It emerges and changes over to IMC conduit for about 100' before it hits the motor. This is the only VFD that comes out of this electrical room that has about a 50-60 motor MCC. We pulled THHN wires from the VFD to the motor un-spliced. Altivar VFDs have an internal line reactor in them so I would think it would filter any unexpected small spikes? Here is a summary of the events that happened, I would appreciate any suggestions.Hey guys,
So, the other strange thing is that we had a 150 hp Altivar VFD in a different electrical building fail about 6 months ago. This VFD is in an electrical room about 300' away, but is fed from the same utility transformer. This one only lost its control board but it happened when it was sitting in stop mode just like VFD #1. I have always seen VFD's protect themselves in the case of a short but two of these VFD's weren't even in run mode when they failed?VFD #1.
Went into commission on 4/20. All startup went well.
The VFD ran for 19 trains which take about 11 hours run time on average, about 209 hours.
The train crew showed up at roughly 6 am on 11/1 and when they went to start the filter fan from the plant PLC HMI it wouldn't start (it hadnt ran in a couple of weeks). The employee went to the adjacent MCC room and saw the breaker was tripped. When he went to reset it the VFD bucket blew up. When I opened this VFD casing up I saw had an obvious line side short. We were not able to analyze the last fault occurred so we do not know the direct cause. The breaker inside the bucket had parts rattling around so it was one hell of a short.
When we wired this system in April, the feeder conductors were pulled through 40' of existing conduit with existing wires. From there we ran new conduit another 100 feet to the new dust filtration system 60 hp motor. My employees that showed up the morning that the VFD failed were the same employees that wired the system in April. Upon arrival they tested the motor, tested the feeder conductors, and opened every enclosure that the conductors passed through to make sure there wasn't an obvious wiring short. All megger measurements were 2g ohms, which is perfect. They borrowed a 60 hp across the line starter from a different motor on site and all started and ran just fine.
VFD #2.
We swapped out the borrowed across the line starter for the new VFD and it went into commission on 11/14. I also changed the breaker inside the bucket that was on the line side of the drive to avoid any chance that this could be part of the problem. All startup went well.
This VFD ran for 7 trains, or about 77 hours.
The train crew ran for roughly 6 hours of a nighttime train on 12/10. This time the filter fan tripped mid-train (roughly 6 hours) at around midnight. When the employee went to reset the breaker on the MCC bucket the same thing happened as the first time, it blew up.
My same employees went over on Monday morning 12/12. They tested the motor, wires, and junctions points the same as before. Everything checked out perfectly like it did the last time. They borrowed the same motor starter as they did the first time and everything has been running fine since.
I reached out to the utility to ask some questions and they offered to put a power monitor on the xfmer. A couple of weeks later they reached out and said that they weren't seeing any odd events going on. I am hesitant to put another VFD in until I figure something out!
Thoughts???