What section of NEC states that the manufacturers recommended fuse sizes must be used to protect the VFD? I am certain I have read this before...
What section of NEC states that the manufacturers recommended fuse sizes must be used to protect the VFD? I am certain I have read this before...
I think Article 110.3 is enough to prove that the VFD manufacturer's recommended fuse size must be used to maintain the UL Listing.
Thanks
The PowerFlex 40 does not provide branch short circuit protection. This
product should be installed with either input fuses or an input circuitbreaker. National and local industrial safety regulations and/or electrical
codes may determine additional requirements for these installations.
Fusing
The PowerFlex 40 has been UL tested and approved for use with input
fuses. The ratings in the table that follows are the minimum
recommended values for use with each drive rating. The devices listed in
this table are provided to serve as a guide.
Recommended Fuse Type: UL Class J, CC, T or Type BS88; 600V (550V) or
equivalent.
I know it appears a bit confusing, but remember that not all areas of the country require NRTL listing (i.e. UL). So here's what it is saying:The device itself is listed reqardless of whether you put the right fuses in place or not.
Incidentally, has anyone ever seen a VFD manual that says you can use circuit breakers instead of fuses?
Here is what a typical AB manual says.
It goes on to say:
The use of the word guide seems to imply they are optional and use of the word minimum implies they can be larger.
The table this is a note to is for using certain AB motor circuit protectors, so it would appear not to apply generally.
As best I can tell by reading the AB manual for this drive, unless you are using a particular motor circuit protector, any CB or fuse on the input suffices.
Most likely, they only want to pay for testing of their devices....their own Buletin 140M motor protectors...I can't explain how they got those listed that way, but it's in their file
Most likely, they only want to pay for testing of their devices.
They could realize a monetary loss if they tested using someone else's circuit breaker. UL testing with fuses, requires a universal umbrella fuse so the manufacturer is not important.
Circuit breakers are not always as slow as many believe, even though they do not meet the strict parameters to be UL Listed as Current Limiting.I was referring to how I was surprised that they could get those little 140M Motor Protector switches listed to protect the VFDs, but not the MCCBs. Before I looked I was expecting it to be fuses only.