Customer with a VFD and an older 200 hp motor. Motor failed showing a ground fault and was. replaced with a similar loaner motor which ran for about a hundred hours when the VFD started showing a ground fault on that one. We ended up going to just South of The Golden Spike to test the second motor. The first took a shot of lightning. No doubt about it from the motor shop. How the VFD survived IDK.
We removed the VFD load wires and tested the load reactor, wires and motor all at one time. We wiggled the wires at the PH, with interesting changes but not a fault. Did both the 1 minute and 10 minute megger checks with the values climbing and dropping repeatedly until it stopped at 1200 mega ohm at the ten minutes. Doing nothing else we wiped the thin layer of dust, dirt, sand from the exposed terminals of the load reactor and along the wires. Did the tests again with both settling in at over 4G within seconds. I expect some change but nothing like that.
We removed the VFD load wires and tested the load reactor, wires and motor all at one time. We wiggled the wires at the PH, with interesting changes but not a fault. Did both the 1 minute and 10 minute megger checks with the values climbing and dropping repeatedly until it stopped at 1200 mega ohm at the ten minutes. Doing nothing else we wiped the thin layer of dust, dirt, sand from the exposed terminals of the load reactor and along the wires. Did the tests again with both settling in at over 4G within seconds. I expect some change but nothing like that.