Received this email from a fountain contractor? Any feedback as far as a solution for the ground fault issue would really help. I have copied the email I received.
justin----cerus vfd drive --ci-030-p2 the in put on drive is 240 volts 1 phase output is 240 volts 3 phase ---we are running a 15 hp 3 phase 230 volt lake fountain motor with this drive ---the motor rpm is 3450 the maximum amp draw is 43.5 amps under running load we are drawing 38.5 amps . power from main to drive is 150 ft away fountain from control panel is 250ft out in lake.
the unit has been running for 3 months fine ---now it is shutting down on vfd ground fault ---have megged out all wirring and they check out ok ------at firdt we disconnected light ground ran fountain it ran for 5 days tripped on ground fault-----disconnected motor and light ground ran for 5 days ripped on ground fault------disconnected ----set vfd ground fault paramater from 5.0 to 1.5 as per manufacturer...---ran unit for 1 day tripped on ground fault---disconnected all ground sources ran unit ran for 2 days trippd on ground fault----we have tryed everything spoke to manufacturer ( ccant give us answer just guesses )
reading the manual it says vfd should not be grounded into control cabinet ground terminal ???????? do they need to be grounded differently why is it tripping if we have no ground hooked upp---i know that not correct but we are trying to figure this thing out i have another drive comming --- just to see if its the drive----this thing driving me nuts help all cable sizzes are correct size as to voltage drops -----motor ok input voltage 240 ok output voltage 240 3 phase ok ??????????????
justin----cerus vfd drive --ci-030-p2 the in put on drive is 240 volts 1 phase output is 240 volts 3 phase ---we are running a 15 hp 3 phase 230 volt lake fountain motor with this drive ---the motor rpm is 3450 the maximum amp draw is 43.5 amps under running load we are drawing 38.5 amps . power from main to drive is 150 ft away fountain from control panel is 250ft out in lake.
the unit has been running for 3 months fine ---now it is shutting down on vfd ground fault ---have megged out all wirring and they check out ok ------at firdt we disconnected light ground ran fountain it ran for 5 days tripped on ground fault-----disconnected motor and light ground ran for 5 days ripped on ground fault------disconnected ----set vfd ground fault paramater from 5.0 to 1.5 as per manufacturer...---ran unit for 1 day tripped on ground fault---disconnected all ground sources ran unit ran for 2 days trippd on ground fault----we have tryed everything spoke to manufacturer ( ccant give us answer just guesses )
reading the manual it says vfd should not be grounded into control cabinet ground terminal ???????? do they need to be grounded differently why is it tripping if we have no ground hooked upp---i know that not correct but we are trying to figure this thing out i have another drive comming --- just to see if its the drive----this thing driving me nuts help all cable sizzes are correct size as to voltage drops -----motor ok input voltage 240 ok output voltage 240 3 phase ok ??????????????