I'm currently working on a water pumping station project and was hoping to get some thoughts or opinions on some VFD options I'm faced with.  The station itself is pretty simple, (2) 500hp, 460VAC Centrifugal Pumps, (2) 50hp Booster Pumps down by the river and about another 100kW or so in misc. lighting, HVAC, etc.  We have a 1500kVA transformer from the utility (480VAC, 1800A service, 2500A Switchgear lineup).  The bulk of the load is obviously the (2) 500hp pumps which will be operated with variable speed drives.  As the A/E involved, we are working with a pump OEM and of course the end user to help assist in procuring the VFD's to drive these pumps.  Originally, we were proceeding with Rockwell PF700, 18-pulse drives but the pump OEM then decided to introduce a "cost effective" alternative by quoting ABB ACS800 drives.  Of course Rockwell then said, well why don't we quote you PF755 6-pulse with harmonic input filters.  I've been told from some people that in water treatment plants, pump stations, etc. 18-pulse drives are the norm these days for meeting IEEE519.  I was just curious if anyone has any opinions or thoughts on the above mentioned drives or perhaps some suggestions that I need to confirm or question to these vendors or utility.  I spoke with the utility and they told me they will meter at the secondary bushings of the transformer and typically look for less then 10% THD.  This seemed pretty high to me.  I'd appreciate any thoughts or suggestions.
I'd also like to just say thank you to all who are involved on this site; I have absorbed a great deal reading these boards every day at lunch.