This is an existing installation.
The rated input current on my VFD is 388A @ 460V.
I currently have a 400A feeder breaker and 2 - 3/0 per phase feeding this VFD. VFD recommended minimum for the input breaker was 600A.
I haven’t had any nuisance tripping of the breaker in the field. I have a feeling that I will have to increase the cable size based on 125% rule. What about the breaker? Do I need to upsize to 600A per NEC? What do you think?