jason.durby
- Tempe, Arizona
- Electrical Superintendent
This is an existing installation.
The rated input current on my VFD is 388A @ 460V.
I currently have a 400A feeder breaker and 2 - 3/0 per phase feeding this VFD. VFD recommended minimum for the input breaker was 600A.