I have been reading previous threads and can't find a definite answer to this question.
I have a 75 hp VFD with an input rating of 96A. Per NEC 430.122, I should size the line side conductor to 125%*96A=120A. This can be done with #1 conductors and #6 ground (will handle 125A).
However, the breaker from the panel serving this VFD is a 150A and the VFD also comes with a 250A thermal magnetic breaker. Which of the following is correct?
1) I can use line-side conductors per NEC 430.122 (handle up to 125A) although the line-side breaker ratings are all higher amperage than what my conductor can handle.
2) I will need to upsize my conductors to handle the OCPD (150A) or replace the OCPD at the feeding panel to be 125A so that my conductors are protected.
I have a 75 hp VFD with an input rating of 96A. Per NEC 430.122, I should size the line side conductor to 125%*96A=120A. This can be done with #1 conductors and #6 ground (will handle 125A).
However, the breaker from the panel serving this VFD is a 150A and the VFD also comes with a 250A thermal magnetic breaker. Which of the following is correct?
1) I can use line-side conductors per NEC 430.122 (handle up to 125A) although the line-side breaker ratings are all higher amperage than what my conductor can handle.
2) I will need to upsize my conductors to handle the OCPD (150A) or replace the OCPD at the feeding panel to be 125A so that my conductors are protected.