Are VFD input conductors permitted to have an ampacity rating that is less than the rating of the protective device upstream?
NEC 240.4(G) states "Overcurrent protection for the specific conductors shall be permitted to be provided as referenced in Table 240.4(G)."
Table 240.4(G) calls out motor conductors - Article 430 Parts II through VII.
Adjustable speed drives fall under 430 Part X.
NEC 430.130(A)(1) for circuits containing power conversion equipment references 430.52(C) in Part IV to size the protective device.
So if the VFD input conductors are sized per 430.122, the upstream SC & GF protective device can have a higher ampacity than the conductors as long as it doesn't exceed the rules in 430.130, correct?