Hi all,
I am putting together a cabinet with (8) 20HP VFD's
Each pump will have a 20hp schneider VFD #ATV320D15N4C with max input current of 45.73A.
Schneiders documentation says Minimum breaker to be 50A but 45.73 * 1.15 = 52.58A which does not meet 430.128.
I want to protect the input of each drive and have a disconnecting means with a circuit breaker. Am i missing something simple here?