rivecar44
Member
- Location
- Chicago IL, USA (MDW)
- Occupation
- Engineer
A vfd manufacturer suggests sizing line side conductors based on the rated inrush current of the device instead of the rated continuous current. Any comments.
Suggestions are not requirements.A vfd manufacturer suggests sizing line side conductors based on the rated inrush current of the device instead of the rated continuous current. Any comments.
for a 125 Hp VFD, input rating 135.8 Amps, max. inrush current 236 amps. Calculating conductor size using 125% per NEC of input rating current equals 169.75 Amps, then 2/O is enough. But, manufacturer suggest minimum 3/O. When I called them, tech indicated the wire range is based on the inrush current.Suggestions are not requirements.
Can you post a copy of this suggestion?
no. only 10 ftLooks like the min size the input lugs accept is 3/0. That makes it easy from here.
Do you expect substantial VD because of distance?
Worst part all drive companies install undersized conductors in their drives. Have performed IR scans in 60 degree rooms where their under sized wire is 20 degrees hotter. When I questioned a drive company they told me that they do not have to follow the NEC. Can still remember the first 100HP VFD that I I stalled in the 1980's. Drive was rated for 135 amps and they only used #2 copper inside of drive and yep they ran hot wasting energy 24/7. I have worked on a lot of motors that years ago were feed from a starter inside of a MCC bucket that where a VFD was installed on feeder wires that were questionable ( Thought they should have been the next guage up wire ) but going by the touch screen panel the output voltage @full speed was usually over 470 volts. We had a lot of drives that had bypass function that would draw a large in rush the infrequent few times they were on bypass. Can remember a drive tech telling me that larger drives ( maybe over 50 HP ) have something built in to limit in rush current on capacitor banks.For a 200 Hp vfd,
for a 125 Hp VFD, input rating 135.8 Amps, max. inrush current 236 amps. Calculating conductor size using 125% per NEC of input rating current equals 169.75 Amps, then 2/O is enough. But, manufacturer suggest minimum 3/O. When I called them, tech indicated the wire range is based on the inrush current.
View attachment 2567440 View attachment 2567441
My guess is the tech does not know and just made up an answer or parroted something some else told him that does not know either. It seems like for some reason they have chosen a MCCB that comes with standard size lugs that just happen to take a minimum size of 3/0.For a 200 Hp vfd,
for a 125 Hp VFD, input rating 135.8 Amps, max. inrush current 236 amps. Calculating conductor size using 125% per NEC of input rating current equals 169.75 Amps, then 2/O is enough. But, manufacturer suggest minimum 3/O. When I called them, tech indicated the wire range is based on the inrush current.
View attachment 2567440 View attachment 2567441
A lot of people selling such things are pump people and know nothing about VFDs, other than that they will solve all known problems with application of pumps and that there are good commissions to be made selling them.Whomever told you that is a nincompoop. Inrush current on a VFD is not a thing worthy of consideration. You might want to find a better supplier, this person is making stuff up…
Agreed.The VFD feeder (input) conductor size is dictated in 430.122, it must be 125% of the rated INPUT current of the VFD, which is usually slightly LESS than the output current rating. If you size it the same as the output conductors, you are safe, albeit possibly wasteful.
There is no upsizing of the conductors involved.Probably the manufacturer cya for excessive voltage drop if it is a long run.
Yes, I know, but it was a boiler plate instruction from the manufacturer.There is no upsizing of the conductors involved.