Trying to figure out if 3 conductors, 250kcmil, XHHW, rated 90 C, inside a conduit is acceptable to use for a motor controlled by vfd. VFD manufacturer recommends wiring rated at 75 degrees. motor full load amps is 225 amps. Table 310.16 shows 290 amps @ 90 degrees, and 255 amps @ 75 degrees. I understand that with the 125% multiplier per NEC the 250kcmil will not be suitable, yet the ampacity rating of the conductors limited by the terminations' temperature rating (75 degrees) is still above the full load amps of the motor.