SiriusC1024
Member
- Location
- Indiana
- Occupation
- Maintenance Supervisor
I've been working on a problem with the VFD/motor combinations used on extruders at our plant. These are 300hp-400hp Baldor RPMAC series motors driven by various VFD's. Whether the drive is a Toshiba, Yaskawa, or Allen Bradley doesn't seem to have an effect. The common cause is the motors themselves. Product literature shows that these RPMAC motors are extremely power dense, and I'm wondering if there are special concerns when it comes to them. These are not the permanent magnet rotor type.
VFD's are set to constant V/Hz mode.
I've identified that the motors are running at high temperatures due to stator saturation. In fact, measuring voltage at the motor terminals using a Fluke 123b oscilloscope shows that the V/hz ratio is in the range of 9V/Hz. The motor nameplate calls for 460V@60Hz, or 7.667V/Hz.
The trick I've done so far is changing the drive parameters to be 460V@66Hz to bring the voltage down to the correct levels at the motor terminals. It's proven effective. For example, a 400hp motor was shown to have a 23kW reduction in power consumption, which was almost entirely iron losses. Basically, that amount of heating is equivalent to 23 space heaters set on high. Temperatures dropped from 220F to 185F.
Still, I'm uncomfortable with this hack. I want to know why this is happening. Looking at a pulse from the drive, the reason for the high V/Hz ratio can be seen. The pulse isn't a clean square wave. There are large overshoots, and the area under them is what's boosting the voltage reading. Now what is going on here? Impedance mismatch would explain the rapid oscillations, but the large-area overshoots?
I have an image of the pulse, but I can't figure out how to upload it. https://photos.app.goo.gl/xcCNFDBHhwm3tvU16
VFD's are set to constant V/Hz mode.
I've identified that the motors are running at high temperatures due to stator saturation. In fact, measuring voltage at the motor terminals using a Fluke 123b oscilloscope shows that the V/hz ratio is in the range of 9V/Hz. The motor nameplate calls for 460V@60Hz, or 7.667V/Hz.
The trick I've done so far is changing the drive parameters to be 460V@66Hz to bring the voltage down to the correct levels at the motor terminals. It's proven effective. For example, a 400hp motor was shown to have a 23kW reduction in power consumption, which was almost entirely iron losses. Basically, that amount of heating is equivalent to 23 space heaters set on high. Temperatures dropped from 220F to 185F.
Still, I'm uncomfortable with this hack. I want to know why this is happening. Looking at a pulse from the drive, the reason for the high V/Hz ratio can be seen. The pulse isn't a clean square wave. There are large overshoots, and the area under them is what's boosting the voltage reading. Now what is going on here? Impedance mismatch would explain the rapid oscillations, but the large-area overshoots?
I have an image of the pulse, but I can't figure out how to upload it. https://photos.app.goo.gl/xcCNFDBHhwm3tvU16