He is.
Danfoss does not make a VFD that will double the voltage from 240V to 480V. Although it is POSSIBLE to make one, it would cost more than using a transformer, so nobody does it.
Nor does Danfoss make a VFD that can accept single phase input without de-rating the drive (above 2HP), and although as a generalize rule, many people SAY that drives can be used at a 50% derate, that is not universally true and you must check with the manufacturer first.
And just to give you fair warning: In the case of the VLT Aqua drives, Danfoss** never tells you the amount of derating it requires, it just says that when it detects an imbalance in the incoming 3 phase, it will automatically derate the drive by lowering the output speed until it is OK with it, but without saying how much that will be, other than it might be anywhere between 50% and 100% of the drive current rating. I did one a while ago with a 50% derate and it would not allow the pump to get past 75% speed. We had to go with a 65% derate to get full speed out of it.
** The DISTRIBUTOR told us we could use a 50% derate, but when it didn't work, DANFOSS said they never claimed that and that it doesn't say that in their manual (which is correct). The distributor had to eat the extra cost to get us the larger drive, I had to eat the extra time on the jobsite because of it (and had to pull larger conductors because of the VFD size being larger to meet 430.122)