VFD nuisance tripping

Status
Not open for further replies.

Saleh

Member
Location
Saudi Arabia
We are facing nuisance tripping after installing new VFD to control an old motor
The VFD is Schneider ATV61HD75N4 75KW, 3P, 380-480V, 50/60Hz.
The Motor is US Motor Catalogue H100E2ES Model #R925.
The connection between the VFD and the motor is copper cable (3X70mm+35mm) in RGS conduit and it is about 40Meter. The fourth core 35mm of the cable used as grounding.
The error message on the VFD says Impedance Sh Circuit.
Otherwise that VFD is much noisier than others with lower Wattage.
How we can solve the nuisance tripping problem?
Does the Motor Choke VW3A5104 will solve it?
Awaiting your comments
:)
 

Attachments

  • Name plate.pdf
    99.1 KB · Views: 0

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
It means you have a short circuit either inside of the VFD, i.e. one of the transistors is shorted, or you have a short circuit in the motor circuit somewhere. You can run a diagnostic of the transistor status from the front keypad, in parameter section 1.10. If they all check out OK, then you have a problem in the wiring to the motor or the motor windings themselves. My money is on the motor windings.

One thing that happens a lot with installing VFDs in old motors, is that the old motor insulation was leaking to ground or phase-to-phase, but the short was of high enough impedance that the Across-the-Line (DOL to you) starter did not trip out because the total current was still below the overload relay trip threshold (often exacerbated by people thinking the OL is bad and "tweaking" it so that is quits tripping).

But the VFD has to be much more careful about things like that and will not tolerate it because it can damage the transistors. Hence the VFD becomes a "fault finder". The problem was already there, you just were not aware of it yet.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If they all check out OK, then you have a problem in the wiring to the motor or the motor windings themselves. My money is on the motor windings.
One thing that happens a lot with installing VFDs in old motors, is that the old motor insulation was leaking to ground or phase-to-phase, but the short was of high enough impedance that the Across-the-Line (DOL to you) starter did not trip out because the total current was still below the overload relay trip threshold (often exacerbated by people thinking the OL is bad and "tweaking" it so that is quits tripping).
I have also heard the assertion that the pulsed waveform from a VFD can cause a greater strain on the motor insulation causing a breakdown which would not happen with sinusoidal voltage. Have you experienced that or is it a wive's tale?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I have also heard the assertion that the pulsed waveform from a VFD can cause a greater strain on the motor insulation causing a breakdown which would not happen with sinusoidal voltage. Have you experienced that or is it a wive's tale?
Sort of. Under the right circumstances, the high speed of the transistor fired DC pulses can interact with the output cables in a capacitor-like fashion to create charges of high voltage that reflect back and forth between the drive and the motor in waves, it's called the "reflected (or standing) wave phenomenon". It's well studied and accepted, yet not completely understood yet. What we do know however is that if there is enough distance, the reflected waves build up a voltage that eventually exceeds the dielectric withstand voltage of the motor insulation and finds the weakest point. That is usually the "first turn" in the windings, where the insulation first gets stretched a little thinner as it bends. What happens then is that you get microscopic "punch-throughs" of voltage between the adjacent phase windings and it gets worse and worse over time until the windings short completely and fail. This can happen in as little as 2 weeks (my shortest experience) or could take years, there are a lot of factors that go into it. There are several things you can do to mitigate this, one of which is to always use shielded motor lead cable. We here in the US have only recently started this, but in IEC world they have been for a long time, because they tended to not use conduit as much as we do. If you but "inverter duty" motors now, most mfrs have upped the ante on the motor winding insulation as well. in the past, the voltage rating was 2X the maximum voltage level, so 600V class motors had 1300-1800V insulation. The voltage spikes can however exceed 2200V now on a 460V rated motor run by a VFD, so a lot of magnet wire mfrs have begun selling it with 2400-4000V insulation.

In this case though, he used RGS conduit and what he referred to as "multi-core" cable, but maybe not shielded. Still the damage would not be instantaneous. My interpretation was that they had an old motor and just installed a new VFD, but the VFD is tripping right away. In that case, I think the motor winding damage was already there.
 

Besoeker

Senior Member
Location
UK
I have also heard the assertion that the pulsed waveform from a VFD can cause a greater strain on the motor insulation causing a breakdown which would not happen with sinusoidal voltage. Have you experienced that or is it a wive's tale?
It's real.
Been there. Done that. In real life.
 

mike_kilroy

Senior Member
Location
United States
I have also heard the assertion that the pulsed waveform from a VFD can cause a greater strain on the motor insulation causing a breakdown which would not happen with sinusoidal voltage. Have you experienced that or is it a wive's tale?

You can do the math and answer this yourself also....

480vac across the line = 480*1.4=672v Peak across any winding every cycle.

480v thru vfd =480*1.4*2= 1344v Peak across any winding every cycle.

Long cable lengths on vfd and 480*1.4*3.x= 2000+ Peak across any winding every cycle.

Does this strain your motor insulation?

I have seen motor insulation failure in less than 5 minutes of on time, many times (many = more than 10).
 

oregonshooter

Member
Location
OR. USA
At double peak voltage you would think all 600v insulation would fail fairly quickly wouldn't you?

Every drive in our plant is running standard motors from 10hz to 120hz on VFDs and no insulation failures would I attribute to the VFD in the past 15 years.

Put me down for "wives tale" on this one. I'm sure on paper it makes sense, in the field I haven't seen it happen or it took so long I didn't attribute a failure to it. Most of our motors cook from lack of cooling and overloading but that's still a multiple year scenario.

Does the motor meg out? The leaking current theory not being noticed on the DOL is what I would look at. You mentioned the ground so I'm assuming this is not an ungrounded system.
 

Besoeker

Senior Member
Location
UK
Put me down for "wives tale" on this one.
Then you'd be incorrect.

I have come across the problem in the field on a few occasions.

Here's a couple of excerpts from a report I wrote for one site:

Rate of change of voltage (dv/dt)
Rate of change of voltage was very fast. In all cases it was either outside the limits of the IEC TS60034-17 technical specification, or marginal. For the rise times measured the maximum dv/dt should not be greater than approximately 1600V/us. The average dv/dt measured at the pump house was 2500V/us.


The motors in question were dying like flies. Within weeks.

Conclusion
The insulation failures have the appearance of partial discharge failures such as would be created by the very high electric field intensity caused by the very fast dv/dt. The recorded dv/dt is as high as any we have measured at or close to the motor terminals.
In summary, the installation of dv/dt filters to reduce the rate of change of voltage applied to the motor is highly recommended.


The recommended filters were installed. And the problem went away.
 

mike_kilroy

Senior Member
Location
United States
At double peak voltage you would think all 600v insulation would fail fairly quickly wouldn't you?

Put me down for "wives tale" on this one.

1) Here is picture of the 1400+ voltage ALL your 460v vfd's are putting in your motors - even if the motor leads are only 1 foot long.

480V vfd motor voltage.jpg

ref: http://www.transcoil.com/Public/Documents/Brochures/KMG-Brochure.pdf


2) Here is what SOMETIMES is put into a motor if long leads etc: ref: Siemens spindle motor spike data from real machine a few months ago.

3200V SPINDLE SPIKES.jpg

3) I ran a test for a customer training class & forgot and fed a 230V 3ph induction motor with 230V insulation off a 480v VFD - for about 3 minutes - before the motor insulation shorted. Motor had 600v insulation (for 230v, not 480v). Luckily it was my motor.

4) I once had to go across country to solve a motor failure issue where windings were shorting out in 5min - 4 hours (no load, not turning) - while others tried to find the problem they popped 12pc $ 6000.00 motors in the two weeks before I was called: found output loose connection that caused 3200v spikes randomly: the 460v motor insulation was rated for repeated hits to about 2500v max - above that and the insulation breaks down faster and faster the higher the voltage.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
At double peak voltage you would think all 600v insulation would fail fairly quickly wouldn't you?

Every drive in our plant is running standard motors from 10hz to 120hz on VFDs and no insulation failures would I attribute to the VFD in the past 15 years.

Put me down for "wives tale" on this one. I'm sure on paper it makes sense, in the field I haven't seen it happen or it took so long I didn't attribute a failure to it. Most of our motors cook from lack of cooling and overloading but that's still a multiple year scenario.

Does the motor meg out? The leaking current theory not being noticed on the DOL is what I would look at. You mentioned the ground so I'm assuming this is not an ungrounded system.

Just because insulation is rated 600 volts doesn't mean it can't take more than 600. Double the voltage and you will probably start to have insulation break down, but it takes time before total failure. Now add some distance to the circuit and that doubled voltage becomes even higher increasing the rate of breakdown of the insulation. This is why the problem is more common with long conductor runs.

If you run same motor (with dual voltage leads) at the low voltage you have reduced the amount of peak voltage to being much closer to the 600 volts insulation rating, and this is why the problem doesn't appear very often with 208 and 240 volt connected motors, even with somewhat longer conductors.
 

mike_kilroy

Senior Member
Location
United States
and keep in mind too this is a corona discharge issue. so that Nema 600v 'rating' takes it into account and it probably means the motor insulation is rated to 1000 or so volts anyway (ref - see nema table 5-7 in attached spec).

It is a cumulative effect; each hit that causes corona causes any air in between windings to ionize and this ionized air eats varnish. Little by little. big spikes eat faster than little spikes. This too is why vacuum impregnated varnish insulated motors are usually good to higher voltage spikes than just dip tanked motors.


ACadjustable in clulding corona info.pdf - Foxit Reader - [ACadjustable in clulding corona info .jpg ACadjustable in clulding corona info.pdf - Foxit Reader - [ACadjustable in clulding corona info..jpg
 

robbietan

Senior Member
Location
Antipolo City
We are facing nuisance tripping after installing new VFD to control an old motor
The VFD is Schneider ATV61HD75N4 75KW, 3P, 380-480V, 50/60Hz.
The Motor is US Motor Catalogue H100E2ES Model #R925.
The connection between the VFD and the motor is copper cable (3X70mm+35mm) in RGS conduit and it is about 40Meter. The fourth core 35mm of the cable used as grounding.
The error message on the VFD says Impedance Sh Circuit.
Otherwise that VFD is much noisier than others with lower Wattage.
How we can solve the nuisance tripping problem?
Does the Motor Choke VW3A5104 will solve it?
Awaiting your comments
:)

is it me or did I just see the motor rated 100HP and a 75kW VFD running it?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
is it me or did I just see the motor rated 100HP and a 75kW VFD running it?
Very nice observation. It sure looks that way if the motor P/N is correct.
But if you use Google, it will tell you that 100HP = 75kW. :happysad:
I wonder whether somebody at the factory did that?
 