I am looking for some help on sizing the cable between my motor controller, a VFD in this case, and the branch OCPD feeding it. Came across a situation at a customer site where they have a 250HP, 480vac motor fed by a VFD. The VFD is fed by a single set of 500mcm cables which meets the 125% of drive rated current (NEC 430 part X). The issue is the branch OCPD is 800amp fuses which I believe violates table 430.52(C)(1) which should be a max of 175% with time delay fuses (approx 525amps). They said they aren't going to pull more cable to the VFD but may look at changing the fuse to a 600amp.
My question is how do you properly size the conductors between the OCPD and the motor starter? Is it based on the 125% of the VFD rated input current or the OCPD? I understand thermal protection is provided by the VFD/starter but it feels wrong to have a single set of 500's on a 600amp OCPD.
The second question is the max rating of fuse. NEC seems to limit it to the 525amp mentioned above, but an Allen Bradley VFD lists the max dual element fuse for a 250HP as 675amps.
My question is how do you properly size the conductors between the OCPD and the motor starter? Is it based on the 125% of the VFD rated input current or the OCPD? I understand thermal protection is provided by the VFD/starter but it feels wrong to have a single set of 500's on a 600amp OCPD.
The second question is the max rating of fuse. NEC seems to limit it to the 525amp mentioned above, but an Allen Bradley VFD lists the max dual element fuse for a 250HP as 675amps.