Hi All -
I have a boat hoist that is powered by 2 single phase capacitor start induction motors.
The controller (up/down only) is wired with 220v from the panel through twin contactors with one of the hot legs being constant (orange) and the other switched to separate motor leads for forward and reverse based on up/down toggle (red/black).
The fixed rotor current is 33A (66A total) for each motor which is marginally greater than the maximum pass through current of the Inverter (60A) - resulting in shutdown due to Max Over Current Error. The grid at the location is incredibly unreliable so switching that load to the utility isn't practical.
I am looking for any suggestions for limiting LRC for a few milliseconds to get the motors to SFA of 6.8A each.
Can a soft starter work here or will torque not be sufficient to start the motors under load (FLT 3 ft-lbs, LRT 9 ft-lbs)? If so, How would I size the soft starter - to SFA or LR? Is the SS device upstream of downstream of the contactors? If downstream, does each of the 3 legs need its own device?
I have yet to find a single phase in/out VFD that would work in this application and replacing the motors with 3 phase would be more expensive than switching out the Inverter. Let me know if you have seen anything different.
All of the precious threads on this have been incredibly helpful in getting me this and am hoping you can fill in the missing details detailed above.
Thanks in advance for any insight you can provide.
I have a boat hoist that is powered by 2 single phase capacitor start induction motors.
The controller (up/down only) is wired with 220v from the panel through twin contactors with one of the hot legs being constant (orange) and the other switched to separate motor leads for forward and reverse based on up/down toggle (red/black).
The fixed rotor current is 33A (66A total) for each motor which is marginally greater than the maximum pass through current of the Inverter (60A) - resulting in shutdown due to Max Over Current Error. The grid at the location is incredibly unreliable so switching that load to the utility isn't practical.
I am looking for any suggestions for limiting LRC for a few milliseconds to get the motors to SFA of 6.8A each.
Can a soft starter work here or will torque not be sufficient to start the motors under load (FLT 3 ft-lbs, LRT 9 ft-lbs)? If so, How would I size the soft starter - to SFA or LR? Is the SS device upstream of downstream of the contactors? If downstream, does each of the 3 legs need its own device?
I have yet to find a single phase in/out VFD that would work in this application and replacing the motors with 3 phase would be more expensive than switching out the Inverter. Let me know if you have seen anything different.
All of the precious threads on this have been incredibly helpful in getting me this and am hoping you can fill in the missing details detailed above.
Thanks in advance for any insight you can provide.