VFD or Soft Start Single Phase Motors

rlay002

Member
Location
Michigan
Occupation
Retired
Hi All -

I have a boat hoist that is powered by 2 single phase capacitor start induction motors.

The controller (up/down only) is wired with 220v from the panel through twin contactors with one of the hot legs being constant (orange) and the other switched to separate motor leads for forward and reverse based on up/down toggle (red/black).

The fixed rotor current is 33A (66A total) for each motor which is marginally greater than the maximum pass through current of the Inverter (60A) - resulting in shutdown due to Max Over Current Error. The grid at the location is incredibly unreliable so switching that load to the utility isn't practical.

I am looking for any suggestions for limiting LRC for a few milliseconds to get the motors to SFA of 6.8A each.

Can a soft starter work here or will torque not be sufficient to start the motors under load (FLT 3 ft-lbs, LRT 9 ft-lbs)? If so, How would I size the soft starter - to SFA or LR? Is the SS device upstream of downstream of the contactors? If downstream, does each of the 3 legs need its own device?

I have yet to find a single phase in/out VFD that would work in this application and replacing the motors with 3 phase would be more expensive than switching out the Inverter. Let me know if you have seen anything different.

All of the precious threads on this have been incredibly helpful in getting me this and am hoping you can fill in the missing details detailed above.

Thanks in advance for any insight you can provide.
 
Rather that retype all of this, I’ll just redirect you to this post:

As to VFDs, it’s similar problem. There ARE VFDs out there for single phase motors, but not YOUR TYPE of single phase motor.

Most likely, your only options are a bigger inverter, or change out the motors to 3 phase and use VFDs.
 
Thanks. I read that post and was leaning towards replacing the motors and adding a VFD is the way to go. The comparable 3P motor lowers the inrush current substantially.

If I go this route, how do I deal with the 220v contactors used for the switch? Does the VFD come after the contactor and use the 2 legs from the contactors as it's input. If so, how does the VFD remain powered when the switch isn't engaged to reduce start up time and retain settings.
 
With two motors, you might be able to put them both on the same VFD if they're identical, other folks can give you a better answer on that.

Power-
Run un-switched 240v to the VFD, remove the contactors as no longer needed or wire around them, and connect the VFD output straight to the motors. Wire the up/down buttons to a couple of inputs on the VFD (you'll have to program the inputs for those functions) and wire any limit switches in series with the Up/Down buttons. (There are probably some other parameters that ought to be set, also leaving that for others.)

You'll want some sort of disconnect before the VFD.

Question for others- does this setup need a GFCI? I think it's prudent, boat hoists seem to be problematic.
 
Not sure how that would work with the myriad of switches, levelers and limit switche run through the contactors.

The up/down toggle (whether wired or wireless remote) is really forward/reverse with the 3P contactor switching L1 between the T5/8 motor lead using the Red/Black contactor outputs. The other contactor output (orange) is always hot when the switched in either direction.
 