mstrlucky74

Senior Member
Location
NJ
Have a spec that reads all vfd OUTPUT circuits to be inXHHW. Would the output wires be the wires from the panel to the vfd withintegral disconnect or from the vfd/disconnect to the motor? Thanks.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Anything connected to the VFD output. (On either side of disconnect.)
The main reason is the presence of high, sharp edged, voltage pulses which can stress the insulation in ways that a sine wave of the same nominal voltage will not.

Sent from my XT1585 using Tapatalk
 

mstrlucky74

Senior Member
Location
NJ
So that could or would be the wires on the line AND load side of the vfd/disconnect? So essentially the entire run.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Anything connected to the VFD output. (On either side of disconnect.)
The main reason is the presence of high, sharp edged, voltage pulses which can stress the insulation in ways that a sine wave of the same nominal voltage will not.

Sent from my XT1585 using Tapatalk

No, the output wiring would only be the wiring from the VFD to the motor.
I think what GoldDigger was meaning is that if you have a disconnect on the LOAD side, i.e. within sight of the motor, you still need the XHHW. All the way from the drive to the motor as steve66 said.

Nothing special on the input side, other than the different sizing rule in 430.122.
 

mstrlucky74

Senior Member
Location
NJ
I think what GoldDigger was meaning is that if you have a disconnect on the LOAD side, i.e. within sight of the motor, you still need the XHHW. All the way from the drive to the motor as steve66 said.

Nothing special on the input side, other than the different sizing rule in 430.122.

Thanks.
 