Besoeker would you mind elaborating on that a bit? What is the technical concern with inverter duty?
Please forgive me if I'm repeating stuff you already know. But, since I don't know what you might already know....
The basic circuit arrangement of most variable frequency inverters these days is a rectifier bridge to convert the AC supply to DC and then an inverter bridge to switch it back to AC at the required power frequency.
As you are probably aware, the output voltage from most inverters is a train of square wave pulses at many times the power frequency, typically a few kHz, and with a pulse width modulated pattern. Even though the motor gets a string of square wave pulses, its inductance means that the current can't change quickly and the result is usually a pretty good sine wave current.
But, and there had to be one, inverters generally use IGBTs as the switching devices to produce the train of pulses. The IGBT switching rate is very fast. It takes a fraction of a microsecond to turn on. As a result, the motor winding can get hit with a voltage rise of several thousand volts per microsecond - the dv/dt issue. This induces capacitive currents that would not normally be seen with the very much lower dv/dt of a "clean" sine wave voltage. (i=Cdv/dt).
I sometimes get involved in motor failure problems with inverters.
Here's a bit from one of my reports where motors were routinely failing after just a few weeks operation.
"Conclusion
The insulation failures have the appearance of partial discharge failures such as would be created by the very high electric field intensity caused by the very fast dv/dt. The recorded dv/dt is as high as any we have measured at or close to the motor terminals.
........
In summary, the installation of dv/dt filters (chokes) to reduce the rate of change of voltage applied to the motor is highly recommended."
In the event, chokes were fitted and the problem went away.