Yesterday observed at a client site:
VFD controlled motor in current limiting alarm, clamped at 103A but running. Motor is 5HP, 480 VAC, control signal (4-20) demanding 66 Hz (20 ma) and drive stuck at 55Hz, 194V, and 104A (as indicated on the drive display, no measurements were taken). I believe normal current draw at 66 Hz for that particular motor is 83 A.
The motor appeared to have been running in this condition for some time. They shut off the drive for a few minutes, restarted the drive and motor came up to desired speed and normal current draw.
I am assuming that at some point the last time the drive started/ramped up speed, the current limit value of 110% was not enough to let the motor accelerate past whatever breakaway torque requirements were at that speed, and the motor 'stalled' at some speed less than setpoint? It was a Danfoss drive and no manual or design settings were available, and it wasn't our install. But wondering if this is likely a drive settings issue or a motor issue. The motor / drive combo has been in service for many years and to my knowledge has not had this occur previously.
VFD controlled motor in current limiting alarm, clamped at 103A but running. Motor is 5HP, 480 VAC, control signal (4-20) demanding 66 Hz (20 ma) and drive stuck at 55Hz, 194V, and 104A (as indicated on the drive display, no measurements were taken). I believe normal current draw at 66 Hz for that particular motor is 83 A.
The motor appeared to have been running in this condition for some time. They shut off the drive for a few minutes, restarted the drive and motor came up to desired speed and normal current draw.
I am assuming that at some point the last time the drive started/ramped up speed, the current limit value of 110% was not enough to let the motor accelerate past whatever breakaway torque requirements were at that speed, and the motor 'stalled' at some speed less than setpoint? It was a Danfoss drive and no manual or design settings were available, and it wasn't our install. But wondering if this is likely a drive settings issue or a motor issue. The motor / drive combo has been in service for many years and to my knowledge has not had this occur previously.