yes, it is about what you have to do if supplying multiple motors in order to individually protect each motor, and use the associated control contact to either stop the drive or trigger an external fault input.Will a typical "pass-through" type motor overload properly sense motor current on the load side of a VFD?
The bimetal OL relay responds to the heating effect of total load current whether it is linear or not. So I expect it to respond to motor overload conditions properly.A couple of minor warnings:
IEC bimetal overload relays are known to have issues with heating up disproportionately to the current going through them at lower frequencies and higher harmonics in the output of a VFD.
The most likely explanation is that, for whatever reason, the resistance (not impedance) of the elements is frequency dependent.The bimetal OL relay responds to the heating effect of total load current whether it is linear or not. So I expect it to respond to motor overload conditions properly.
Well, it's a real problem, so just saying that it does not happen is more like religion than engineering.The bimetal OL relay responds to the heating effect of total load current whether it is linear or not. So I expect it to respond to motor overload conditions properly.
My suspicion is a skin effect issue because of the fact that a bimetal OL is, by definition, two dissimilar metals with inherently dissimilar properties relating to heating, so undoubtedly different skin effect responses in those metals that become more pronounced under low frequency. I don't know if anyone has investigated it too much further than to understand that it IS happening, because there is a simple fix.The most likely explanation is that, for whatever reason, the resistance (not impedance) of the elements is frequency dependent.
Skin effect? Magnetic heating?
The bimetal OL relay responds to the heating effect of total load current whether it is linear or not. So I expect it to respond to motor overload conditions properly.
The bi-metal relay responds to the RMS value of the motor load current and so harmonics is no issue for it.Well, it's a real problem, so just saying that it does not happen is more like religion than engineering.
The bi-metal relay responds to the RMS value of the motor load current and so harmonics is no issue for it.
My suspicion is a skin effect issue because of the fact that a bimetal OL is, by definition, two dissimilar metals with inherently dissimilar properties relating to heating, so undoubtedly different skin effect responses in those metals that become more pronounced under low frequency. I don't know if anyone has investigated it too much further than to understand that it IS happening, because there is a simple fix.
I have none because it seems gibberish to me.Do you have a response to the last portion of the post you didn't quote?
The bi-metal relay responds to the RMS value of the motor load current and so harmonics is no issue for it.
I have none because it seems gibberish to me.
Sure, that spec for linear loads. But the industry has found that bi-metal O/L relay works with non-linear loads as well.. Sure, bi-metal overloads are SUPPOSED to react only to RMS current, but look at the specs: at 50-60Hz. No evidence that they have been tested, or approved, for use at any other frequency.
Thermal overload relays work both with alternating and direct currents. US community took to melting alloy type O/L relay and European community to bi-metal relays.Here in the U.S., we still have a few places where 25Hz is still in use (many of the big pumps in New Orleans if anyone was wondering).
Bimetallic OL relays are not used there as well, only melting alloy or very high-end solid state MPRs. I did a project for one of those after Katrina and that's what raised my curiosity. The specs explicitly restricted any OL protection from being anything other than melting alloy or solid state Motor Protection Relays that explicitly show approval at 25Hz (Multilin dies).
Because then there would be a competition between thermal O/L relay and VFD for tripping on overload.A little more delving on my part after reading that dug up warnings from some bi-metal OL relay mfrs about using them behind VFDs .
Yes, multi-motor would be the primary reason, but also if the VFD is much larger than the motor. Most have some lower limit on sizing because of the accuracy of the OL sensing that's built-in. Typically if the motor is less than 1/2 of the amp rating of the drive, you'll want to add an external OL.Modern VFDs provide overload protection already so why would anyone need to add an external overload (multiple motor situations excepted)?
US community took to melting alloy type O/L relay and European community to bi-metal relays.