oceanobob
Member
- Location
- central coast California
- Occupation
- electrical and industrial contractor company owner
Recently a motor (480vac, 900 rpm, 8.6kw, 12 hp, 17.7a, delta connected, 160L frame) installed with a AB VFD. VFD connected to bus using line reactor and motor connected to VFD with 25lf of shielded VFD cable etc. Motor operation is typically loaded to about one third of the rated voltage and about 45% max rpm.
Motor load end drives a coupling to a helical gear that is reaction torque restrained; coupling alignment AOK. Motor position is vertical with load end up.
Motor hours about 4000.
The machine shut off with the VFD in overvoltage alarm. Meggered the motor and it failed right off. Pulled the motor and at the rebuild shop they found the load end outer bearing race in the cast iron housing had spun which allowed the rotor to contact the windings and the windings were failed as shorted to ground.
With this background information - here be the general inquiry:
How would this condition cause an overvoltage alarm on the DC bus at the VFD? or does the overvoltage alarm also indicate other malfunctions??
Motor load end drives a coupling to a helical gear that is reaction torque restrained; coupling alignment AOK. Motor position is vertical with load end up.
Motor hours about 4000.
The machine shut off with the VFD in overvoltage alarm. Meggered the motor and it failed right off. Pulled the motor and at the rebuild shop they found the load end outer bearing race in the cast iron housing had spun which allowed the rotor to contact the windings and the windings were failed as shorted to ground.
With this background information - here be the general inquiry:
How would this condition cause an overvoltage alarm on the DC bus at the VFD? or does the overvoltage alarm also indicate other malfunctions??