kevlarster
Member
- Location
- Zelienople PA
A 100hp, 40hp, & 10hp motor are controlled from a single panel with 3 VFDs in it. The VFDs are rated for 150% of the motor HP. Therefore the VFD ratings total 285 amps. (motors FLA x 1.5)
The 3 motors are intermittent duty and will never operate simultaneously.
The incoming breaker in the panel is rated at 400A, but is SET for 280A.
My question is; Do I have to feed this panel (via 3p Breaker in MCC) with a 400A, or can I use a 300A breaker? I've been told that it depends on whether or not the panel breaker's trip setting is readily accessible or not.
Any help is greatly appreciated.
Kevlar8)
The 3 motors are intermittent duty and will never operate simultaneously.
The incoming breaker in the panel is rated at 400A, but is SET for 280A.
My question is; Do I have to feed this panel (via 3p Breaker in MCC) with a 400A, or can I use a 300A breaker? I've been told that it depends on whether or not the panel breaker's trip setting is readily accessible or not.
Any help is greatly appreciated.
Kevlar8)