My 12 year old AD GS2-23P0 vfd will give me the power Factor Angle. How do I convert that to Power Factor?
There are essentially two different power factors. There is the input side of the VFD. Usually we made the input side 0.9 pf. For that you need the current essentially a 120 degree on the first cycle and -120 deg in the other half. The output of the VFD is variable PF depended load. If it is at full load it is typically 0.8 PF. We have had a few that were 8-pole motors and these were 0.70 PF or lower.My 12 year old AD GS2-23P0 vfd will give me the power Factor Angle. How do I convert that to Power Factor?
That's the definition of power factor.So I'm guessing the PF = Cosine (Angle).
That is for a linear function. VFDs are not linear.My math is a little rusty, but it has to be one of the trig functions. And the cosine is the only trig function that gives the correct answer for those two points.
So I'm guessing the PF = Cosine (Angle).
That's the definition of displacement power factor, to be pedanticThat's the definition of power factor.
If we are talking about the power factor of the driven motor that is going to be linear or darn close to linear.That is for a linear function. VFDs are not linear.
To be even more pedantic, I believe it's not a definition, but rather a formula for calculation for an ideal sinusoidal waveform.That's the definition of displacement power factor, to be pedantic
For just the motor, yes. But how useful is that for the system voltage ?If we are talking about the power factor of the driven motor that is going to be linear or darn close to linear.
The rather inexpensive AD drives like OP has probably won't tell you much of anything about what is going on with the input leads. DC bus and beyond is all that they monitor or control. Only clues about input problems is if they cause DC bus voltage to drop too low.
Is not. But the thing is like I said, with these lesser expensive drives there is nothing really monitoring anything on the input lines, just the DC bus and beyond. So nothing all that useful built into them for anything involving system voltage other than if something happens that causes a drop in DC bus voltage, but all that does is alert you the bus voltage is too low and you still need to figure out why. Bus overvoltage is one other somewhat common problem, is usually encountered when there was a blip in supply voltage while the motor was running and it was not able to successfully restart "on the fly".For just the motor, yes. But how useful is that for the system voltage ?
I'm sure you are right. We did mostly industrial and everything was monitored.Is not. But the thing is like I said, with these lesser expensive drives there is nothing really monitoring anything on the input lines, just the DC bus and beyond. So nothing all that useful built into them for anything involving system voltage other than if something happens that causes a drop in DC bus voltage, but all that does is alert you the bus voltage is too low and you still need to figure out why. Bus overvoltage is one other somewhat common problem, is usually encountered when there was a blip in supply voltage while the motor was running and it was not able to successfully restart "on the fly".
The drive shows the voltage of the fundamental sine wave component of the PWM output, which is the useful component for the motor. The Fluke 87 is likely responding to all of the high frequency components of the PWM waveform, and its RMS response is also likely overweighting the peaks of the switching noise. Therefore it will read much higher than the drive shows. There are meters that have a lowpass filter that can be engaged to make them more accurate for measuring VFD outputs.The one thing that bothers me is the output voltage. The Drive says 103 volt but my fluke 87 says 164 volt. I'm missing something there.
Changes answer to.537 Kw and .72 Hp.)
Older model 87s. I wish I still had the Simpson. It walked away.If you have the Fluke 87V model it has a low pass filter that should give you close to the value the drive is giving you. If you have older model like 87-III without filter, use the Simpson or another digital meter with low pass filter enabled if available.