I wasn't on site but a coworker (hvac tech) called me about a problem. Cooling tower with 2 fans on VFDs, not sure on size ,around 20HP, 208 volts. Been running fine for about 2 plus years.
While there he was asked to look and see why the breaker for the 1 fan was tripping. He found that both breakers were "too hot to touch"
The setup: Breakers in panel in basement, VFDs right beside panel, load to cooling tower on roof are each run in separate conduits- about 50', there are no other wires in conduit to roof
He says everything about this setup is HOT, pipes to roof, conductors in pipe, disconnects on roof, sealtite, and the motors.
He checked amps with meter, below FLA and the vfd amps agreed with his meter.
VFDs are not showing any faults, I think they are Yaskawa
Only the 1 breaker has tripped several times, the facility maint. cleaned the vfd filters, apparently they were quite dirty.
Coworker told them they needed to get their electrician involved so they called the control contractor :?:?
He said they are having quite a bit of major electrical work being done at the facility right now.
Addendum.. Site electricians changed both breakers, did not make any difference ,still very hot
sorry for second hand information, but any ideas what could be causing this??
While there he was asked to look and see why the breaker for the 1 fan was tripping. He found that both breakers were "too hot to touch"
The setup: Breakers in panel in basement, VFDs right beside panel, load to cooling tower on roof are each run in separate conduits- about 50', there are no other wires in conduit to roof
He says everything about this setup is HOT, pipes to roof, conductors in pipe, disconnects on roof, sealtite, and the motors.
He checked amps with meter, below FLA and the vfd amps agreed with his meter.
VFDs are not showing any faults, I think they are Yaskawa
Only the 1 breaker has tripped several times, the facility maint. cleaned the vfd filters, apparently they were quite dirty.
Coworker told them they needed to get their electrician involved so they called the control contractor :?:?
He said they are having quite a bit of major electrical work being done at the facility right now.
Addendum.. Site electricians changed both breakers, did not make any difference ,still very hot
sorry for second hand information, but any ideas what could be causing this??