Coming to PD sizing ???
I have this VFD used on a 400HP motor with 477A FLA Per 430.250.
VFD rating 411-519kVA with input amps max of 655A.
If I use 2-500MCMper phase i will have 427*2*0.88=751A
This is not going to work because instead of sizing conductors to motor FLA i am sizing for the VFD FLA which is 655*1.25=818A min
For this i need 3*350MCM =283*3= 849 really? i am assuming this cables to be sized like this all the way to the motor? Are we sizing this way just because VFD has the ability to connect higher motor sizes?? If so can i size conductors based on HP if it is changed the conductors to be changed as well for later??
PD sizing: if it has to be sized for the cables it has to be 800A. correct.
Now the overload settings in the VFD is 1.15 to motor or 1.15 to the VFD?
Option 1: If i do the overload 1.15*motor which is 1.15*477=548.5A. my protection device size has to be greater than 548.5 and below 849A so can i size 600A breaker. this way breaker is sized more than overload and protecting conductors. But if the motor is changed in the future breaker and overload to be changed as well.
Option 2: If i do the overload 1.15*VFDr which is 1.15*655=753. my protection device size has to be greater than 753 and below 849A so can i size 800A breaker. this way breaker is sized more than overload and protecting conductors. but there is no overload protection for the motors.
Option 3: Adjust the overload based on the motor and size thePD based on the condutors max of FLA of the VFD but not exceding it.
Please correct me which option is the best way to go by.
Thanks in advance.