VFD Protection

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Elementary question.
If a VFD nameplate calls for 200 max overcurerrent protection, is there any allowance that allows you to feed it with a conductor smaller than 3/0
(The motor is 100 HP/480v)
 
Its not given, but for conversation sake lets say 175 amp
Then 430.122(A) will require a conductor ampacity of 218.75 amps, requiring 4/0 copper. Note that if the horsepower rating is greater than 100 hp, the VFD instructions may provide a lower input amp rating for the 100 hp motor.
 
Top