On a recent project installation, the engineer specified the use of VFD cable [shielded, 3-symmetrical grounds, etc.] to be installed in RMC from the drive to the motor [less than 125’ in my opinion belts and suspenders], at the motor there is also a local non-fused safety switch. Wanted to get opinions from others as how they addressed correctly grounding the conductors. The drive manufacturers indicated the shield / ground conductors need to be continuous from the drive to the motor termination without any intermediate grounding, this also appears to be the stance from the cable manufacturers [still waiting for response from one of the vendors]. So, the question is how to handle this at the local safety switch? If the grounds are continuous can you use the conduit system [provided it is properly installed with the correct fittings] as the safety switch ground or would [as this engineer recommended] install a separate 600V ground conductor in the conduit with the VFD cable for safety switch grounding, making the pull much more difficult with the VFD cable and a separate ground conductor…thoughts??