VFD rated motors

Status
Not open for further replies.

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Will a VFD rated motors run or react differently with a across the line full voltage motor starter
Depends on what vintage. If you are comparing the latest highest efficency vfd rated motor to a 50 year old unit the answer is that the starting current on new motor when started across the line might be double the old one. Does not have much to do with being vfd rated though.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
In my experience, the VFD rating has to do with winding dv/dt rating.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
And maybe the bearing design to provide positive rotor grounding for switching frequency harmonics without drawing current through the balls and races.
 

bwat

EE
Location
NC
Occupation
EE
I’ve heard the air flow / cooling / fan is also something that can be different with inverter rated/duty motors since at lower speeds it won’t get as much air flow from the fan.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I’ve heard the air flow / cooling / fan is also something that can be different with inverter rated/duty motors since at lower speeds it won’t get as much air flow from the fan.
you can add an external fan to any motor. but usually it is not needed unless the motors will run at full load at very low speeds, or even at zero speed. not real common but not unheard of either. these days most decent motors are going to be suitable for use with inverters anyway.
 