No problem at all just trying to get to the bottom of this rabbit hole so I can be confident in the method.
Jraef
You size the SCPD per the manufacturer's instructions as per their UL listing, that is what it says 430.130 A.2 says.
Inrush Jeff
I am using the 2020 NEC and it looks like the SC and GF protection for a VFD comes from 430.130(A)(1) and that says to refer back to the classic 430.52 where we do appear to use the motor amps but per 430.130(A)(1) (Exception to 1), we get to use the drive amps. Since this drive lists a maximum Class T fuse of 80A it looks like we move to 430.130(A)(2) where it says we cannot exceed that 80A protection. So I believe that makes it our maximum value for the motor branch circuit SC and GF protection. It also looks like we can correctly use a non-delay fuse for that type of protection. I believe that if the drive didn't list a maximum fuse then we could size it 150% to 300% of the drive input rating.
This was from my earlier posts. I was a bit confusing at the end where the 150% to 300% is actually a maximum depending on the type of motor you have and not a range.
Jraef
Their instruction only give you the MAXIMUM size, you can do what you want so long as it is never MORE than that. By the way, 450.52 is also the MAXIMUM size, not the absolute size. Its a rule, not a design guide.
That is an excellent point that those are maximums. So PaulEngr mentioning 125% for SCPD was indeed code compliant. It is as simple as that.
Jraef
I guarantee to you that you that there is no way you can use that drive without fuses if they only list fuses as the SCPD. The fuses will be part and parcel to their SCCR listing, so without using their specified fuses, you will only get a 5kA SCCR and in most industrial environs, you will ahve way more than that available.
I totally agree and it is true that fuses are a big part of the SCCR for drives and that is no different for this particular one. If one wasn't specified by a manufacturer, which would be very rare indeed, then is it true that it would fall to 430.130 A.1 to select the protection from 430.52? If this is true that puts that question to bed.
So that leaves the situation of the input conductors sized for at least 125% of the drive rated current with no need to take into account the SCPD that can be much higher. This is a question that has been very hard to track down an answer for VFDs, very common for normal motors without drives.
Jraef
If that fuse is going to be the Branch OCPD, then yes, you would have to size the conductors to the fuse that you use. But you can use a lower Branch OCPD up stream that protects your #6 and also have the 80A fuses ahead of the drive to satisfy the UL requirements.
Your original reply is what made me confused about this but now I see that you say OCPD and not SCPD. If the 80A fuses specified by the manufacturer are also used to provide ONLY the short circuit and ground fault protection for the motor branch circuit, then do you need to size the input conductors to take that into account? I don't think that is true and they can simply stay at at least 125% of the drive input current. I believe you can use the 6 awg conductors with the 80A fuse and if, for whatever reason, there were no fuse or breaker specified by the manufacturer, you could protect the 6 awg conductors with up to 156A non-delay fuses (52A x 300%) or 130A Inverse Time Breaker (52x250%). There is no need for overcurrent protection from these fuses since that is done in the drive and protects the input and output conductors as well as the motor from long term high loads. Is this correct?