Hello, I believe this should be pretty straight forward. We have a 40hp, 460VAC, 3 phase motor and a nice ABB ACS880 drive rated for 52 input amps. The input conductors would then be 52 x 1.25 is 65A, so 6awg at 75C. Well, the ABB manual lists 80A Class T fuses and 4awg "Power Cables".
I am a bit confused about scenarios where only the input fuse is specified by the manufacturer but perhaps not the conductors. The ABB manual is a bit confusing since they simply say "Power Cables" so it could mean input or output or both, although I would lean towards it meaning only input conductors. If an 80A Class T fuse is specified I don't see how you could use 6awg conductors. Then it makes sense that they list 4 awg "Power Cables". This leaves it looking good to use 6awg for the output conductors to the motor, sized at 125% of the motor FLAs, which is 52A from 430.250. I am way off base here?
Thanks a lot! Jeff
I am a bit confused about scenarios where only the input fuse is specified by the manufacturer but perhaps not the conductors. The ABB manual is a bit confusing since they simply say "Power Cables" so it could mean input or output or both, although I would lean towards it meaning only input conductors. If an 80A Class T fuse is specified I don't see how you could use 6awg conductors. Then it makes sense that they list 4 awg "Power Cables". This leaves it looking good to use 6awg for the output conductors to the motor, sized at 125% of the motor FLAs, which is 52A from 430.250. I am way off base here?