I'm connecting a new exhaust hood and Make Up Air unit for a restaurant. Hood manufacturer supplied VFD's for both. The MUA unit vfd will need to be located remotely, there is no room in housing to mount it. Now I will have a disconnect for the remote vfd and a factory installed disconnect for the motor on the roof. I need to find out if the VFD will get angry and break if someone disconnects the unit on the roof for service WITHOUT ALSO disconnecting the vfd. The VFD is a Lenze i510 protec. Some of the warnings make me think a disconnect on the manufactured phases are bad for the vfd. And if this is the case, what kind of control circuit/relay/shunt breaker would you recommend for the rooftop disconnect to also kill the upstream VFD disconnect.