VFD to motor conductor sizing

Status
Not open for further replies.
Question has come up concerning branch conductor sizing from a VFD to the motor. One source says (per the NEC) that conductors have to match the size of the drive. EG - 300HP drive has to have conductors rated for 300HP from drive to motor.

Argument is that in an industrial setting you may need a 300HP drive for a 225HP motor, therefore the conductors are sized for the 225HP motor. Drive parameters

Comments?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
It depends. The VFD becomes the SCPD for the motor circuit in most cases (some cheap mfrs don't test it that way with UL and instead, bury some little fine print in the installation manual saying that the installer is responsible for the motor SCPD). So if you have a 250HP motor and a 300HP VFD, the motor lead conductors can be sized for the motor. But if you ever changed the motor to 300HP, then you would have to change the conductors too so it's never a bad thing to think ahead if there is any possibility it might change.

But the NEC does say that the LINE side conductors feeding the VFD must be sized for 125% of the VFD Max Amp rating, not the motor connected to it. That may be where the confusion lies.

Side note:
Not sure where you would need a 300HP VFD for a 225HP motor by the way. If the 225HP motor (not that there is such a thing) was insufficient for the load, a bigger VFD would not solve the problem. On really rare occasions you may need a bigger VFD if you need full Breakdown Torque from the motor for longer than the VFD can deliver it, but in most of those cases a standard motor will not be able to deliver it for longer anyway, so you are looking at a complete engineered drive / motor situation. I've seen that on SAG Mills and big centrifuges, but it's not common by any stretch. I know there are people who believe in over sizing everything (and the VFD mfrs love them), but it really isn't necessary most of the time.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Question has come up concerning branch conductor sizing from a VFD to the motor. One source says (per the NEC) that conductors have to match the size of the drive. EG - 300HP drive has to have conductors rated for 300HP from drive to motor.

Argument is that in an industrial setting you may need a 300HP drive for a 225HP motor, therefore the conductors are sized for the 225HP motor. Drive parameters

Comments?

IMO, the wiring betweent the VFD and the motor is motor wiring and should follow the conductor sizing requirements for motors.
 