If a 3ph hvac compressor has RLA of 15 amps but a LRA of 110 amps, would using a VFD as sort of a soft starter to run the compressor reduce or eliminate the high current draw when the compressor starts?
That would surprise me. A three-phase VFD needs 12 semiconductor devices. A soft start can be done with four and can be bypassed once the motor is up to speed to reduce heat losses.Almost true.
First off below around 25-30 HP the prices are very similar especially against a cheap VFD.
Jraef: The OP stated 3ph. You might have misread that as 3 hp?
Is your system giving you problems, or is this theoretical? The high starting current should only be there for a second or so. If it’s longer, there might be something wrong.
If there are large interruptible loads, (water heater, range?) you might interlock them so they're turned off when the compressor wants to start.
You might also look at the mechanical side of the HVAC system.
For example, installing a timer to assure that the compressor remains off for a minimum of five or ten minutes, the system has a chance to equalize high-side and low-side pressures, and the compressor is not asked to start with a large pressure differential imposed on it. Or a solenoid valve that remains open, shunting the compressor discharge directly to its inlet and eliminating any pressure differential, for maybe 10 or 20 seconds until the compressor motor's up to full speed. (if you do that, be sure to get a "slow closing" valve)
If there are large interruptible loads, (water heater, range?) you might interlock them so they're turned off when the compressor wants to start.
You might also look at the mechanical side of the HVAC system.
For example, installing a timer to assure that the compressor remains off for a minimum of five or ten minutes, the system has a chance to equalize high-side and low-side pressures, and the compressor is not asked to start with a large pressure differential imposed on it. Or a solenoid valve that remains open, shunting the compressor discharge directly to its inlet and eliminating any pressure differential, for maybe 10 or 20 seconds until the compressor motor's up to full speed. (if you do that, be sure to get a "slow closing" valve)
Is your HVAC compressor single phase or 3 phase? If it is single phase, then no. There are a couple of VFDs that will work for PSC single phase motors only, but most single phase A/C compressor motors are not PSC and I seriously doubt any hermetically sealed compressor mfr is going to tell you this is OK.
The same might be true of Soft Starters.
Is your system giving you problems, or is this theoretical? The high starting current should only be there for a second or so. If it’s longer, there might be something wrong.
Theoretical fix for an issue experienced in the past. Was trying to run a 3 or 5 ton hvac -I forget the exact size, off a 40kva generator rated at a bit over 100 amps per phase and the generator could barely start the compressor. Looking for a solution other than drastically increasing the generator size.
Theoretical fix for an issue experienced in the past. Was trying to run a 3 or 5 ton hvac -I forget the exact size, off a 40kva generator rated at a bit over 100 amps per phase and the generator could barely start the compressor. Looking for a solution other than drastically increasing the generator size.
If there are large interruptible loads, (water heater, range?) you might interlock them so they're turned off when the compressor wants to start.
You might also look at the mechanical side of the HVAC system.
For example, installing a timer to assure that the compressor remains off for a minimum of five or ten minutes, the system has a chance to equalize high-side and low-side pressures, and the compressor is not asked to start with a large pressure differential imposed on it. Or a solenoid valve that remains open, shunting the compressor discharge directly to its inlet and eliminating any pressure differential, for maybe 10 or 20 seconds until the compressor motor's up to full speed. (if you do that, be sure to get a "slow closing" valve)
40kVA should be well over what is needed for 5 ton of AC, could be a pretty noticeable voltage sag while trying to start though.
What other load was already running may be an issue?
paulengr;n2537158II have not seen SCRs come this way. It’s possible but have not seen one. .[/QUOTE said:They do. Tried Semikron?