Here is my first question:
Is it possible to have 2- 600v load reactors in VFD application each with 5% impedance put together in series to create a 10% load reactor? If this is possible could a person put 3 in series to create 15% impedance?
One of our clients have a 12 year old Toshiba VFD. Although, the motor distance from VFD is not more than 30? they had 9% load reactor installed. The incoming source is 600V and the motor is operating at 480V. Everything was working fine with 9% reactor till they had a ground-fault in load reactor. After that they changed the load reactor but they face the trip all the time. They tried 2% and 5% load reactor but nothing has changed yet.
It can be observed from the trends, there is a normal running one, one with no reactor, and one with 2- 3% reactors in series. Without the reactor they tripped on high current, 250 amps in 4 seconds, with 2 reactors we tripped on high voltage, 480 in 40 seconds. They also tried a single 3% reactor which did nothing. The 2 reactors they put in series were 600v / 250hp / 3% imp.
Do you think the problem is because of load reactors? They have performed megger test and it seems that the motor is just working fine. Do you think the problem is with the drive? Based on my knowledge it is recommended that IGBTs on the back end and Diodes on the front end be replaced after 9 years so maybe they are wearing out and that?s why they are facing overcurrent. Any thoughts on that?
Thanks.
Here is my first question:
Is it possible to have 2- 600v load reactors in VFD application each with 5% impedance put together in series to create a 10% load reactor? If this is possible could a person put 3 in series to create 15% impedance?
One of our clients have a 12 year old Toshiba VFD. Although, the motor distance from VFD is not more than 30? they had 9% load reactor installed. The incoming source is 600V and the motor is operating at 480V. Everything was working fine with 9% reactor till they had a ground-fault in load reactor. After that they changed the load reactor but they face the trip all the time. They tried 2% and 5% load reactor but nothing has changed yet.
It can be observed from the trends, there is a normal running one, one with no reactor, and one with 2- 3% reactors in series. Without the reactor they tripped on high current, 250 amps in 4 seconds, with 2 reactors we tripped on high voltage, 480 in 40 seconds. They also tried a single 3% reactor which did nothing. The 2 reactors they put in series were 600v / 250hp / 3% imp.
Do you think the problem is because of load reactors? They have performed megger test and it seems that the motor is just working fine. Do you think the problem is with the drive? Based on my knowledge it is recommended that IGBTs on the back end and Diodes on the front end be replaced after 9 years so maybe they are wearing out and that?s why they are facing overcurrent. Any thoughts on that?