Customer has two identical auger motors that he wants to control the speed of.
One VFD, with only one of the two motors being online at a time. Product A or Product B. Never both. I anticipate interlocking a couple contactors or starters of adequate size so one or the other must be "On" before the VFD is allowed to start, and VFD "Off" before contactor A or B is allowed to open.
Is a HP rated GP contactor adequate or should I be using a Starter, minus the overload block?
One VFD, with only one of the two motors being online at a time. Product A or Product B. Never both. I anticipate interlocking a couple contactors or starters of adequate size so one or the other must be "On" before the VFD is allowed to start, and VFD "Off" before contactor A or B is allowed to open.