Jody Boehs
- Fairview, Oklahoma, USA
- Controls and Electrical Manager
Hello,
In my facility we have an emulsifier that is powered by a 125 HP Motor. This motor is operated by a soft starter.
This emulsifier is NOT on our backup power system. We are in the very early stages of figuring out if we have enough backup power capability to handle it.
We have 2 600KW Generators that are independent of each other, each with a UPS system that allows them to start up and transfer without any loss of power in the plant. Each of these units are running at about 50% capacity during the summer (this decreases during the winter).
My main question, however, is as follows:
This emulsifier has an inrush current of 830+ amps. We were told by our Generator vendor that we would need another 600KW Generator to handle that inrush (Keep in mind this 125 HP motor starts and stops approximately 10-15 times per 24 hrs).
Would a VFD instead of a soft starter on that motor reduce that inrush current?
Thank You!
Thank You!