Hi all, I designed the remodel of a courthouse that has an existing delta high leg service. We are not touching the service and are adding a few three phase motors (air handlers etc). In the field someone on the mechanical side has raised the concern that the supplied VFDs don't work with a delta high leg - more specifically that they need to be upsized by like a factor of two to work. I do not believe this is correct, but as delta high legs aren't something I run into every day thought I should run it by you guys.
We are talking about 5 HP motors. The VFDs are ABB ACH550 models and are rated from 208V to 230V +/- 10%.
I read some chatter that if the high leg is generated by two pole mounted utility transformers it could cause trouble. We have a fairly new pad-mounted service here, not sure the particulars of what is inside the box but if there is a concern I can ask.
Any insight?