I need to feed a new 100HP compressor with built in VFD. The installer wants me to install fast acting fuses to protect the electronics.
The testing paper I received from the manufacture calls for the main power supply to be 460V, and Max fuse of 160A.
The main tag on the compressor in the other hand call for 3ph 380-460V, FLA is 178/147A. The largest motor FLA 164A.
How would I calculate this compressor? Should I provide 160A fast acting fuse since it's being controlled by VFD? or should I calculate 164A* 300% for fast acting fuse?
Any suggestion please!