RussWatters
Member
- Location
- Trappe, PA, USA
Hi guys, first time poster. I'm an HVAC/mechanical engineer and my question relates to a VFD/motor sizing mismatch issue and how the NEC's logic (or lack thereof?) applies.
The issue is with a fan replacement utilizing an existing VFD. I decided the existing fan motor didn't have enough safety factor from the original design and bumped it from 50 HP to 60 HP. An apparent miscommunication between me and the electrical engineer resulted in them reporting back to me that the existing motor and VFD were 60 HP. We are resolving the issue by replacing the VFD (and all associated wiring, breaker, etc.).
It's more complicated than that, but close enough...
My question relates to the logic for matching VFD and motor sizes. My understanding is the VFD has to be rated for at least the horsepower of the motor, but can't be rated for less. Given that the existing system is functioning fine and drawing less than 50hp, just installing a 60hp motor and fan wouldn't actually change anything about the operation and the motor doesn't know its own size: it just spins and the load applies a torque to it. It appears to me that from a practical standpoint, nothing has changed.
Because motors are dumb, my usual concerns involve accidental over-amps. Wrong sheave size, turning on a fan without a duct attached -- ironically, too much static pressure safety factor -- accidental overspeed of a direct drive fan with a normal operating speed below 60 hz, etc. The conditions I put the motor on are what determine the break horsepower and therefore amp draw. The motor's actual size has very little to do with that: it either provides what the fan demands or fails trying (by its protection device).
The code says, so we do, but am I missing something in the logic? Is the code requirement here simply a matter of simplicity/consistency as opposed to combating an actual safety concern?
The issue is with a fan replacement utilizing an existing VFD. I decided the existing fan motor didn't have enough safety factor from the original design and bumped it from 50 HP to 60 HP. An apparent miscommunication between me and the electrical engineer resulted in them reporting back to me that the existing motor and VFD were 60 HP. We are resolving the issue by replacing the VFD (and all associated wiring, breaker, etc.).
It's more complicated than that, but close enough...
My question relates to the logic for matching VFD and motor sizes. My understanding is the VFD has to be rated for at least the horsepower of the motor, but can't be rated for less. Given that the existing system is functioning fine and drawing less than 50hp, just installing a 60hp motor and fan wouldn't actually change anything about the operation and the motor doesn't know its own size: it just spins and the load applies a torque to it. It appears to me that from a practical standpoint, nothing has changed.
Because motors are dumb, my usual concerns involve accidental over-amps. Wrong sheave size, turning on a fan without a duct attached -- ironically, too much static pressure safety factor -- accidental overspeed of a direct drive fan with a normal operating speed below 60 hz, etc. The conditions I put the motor on are what determine the break horsepower and therefore amp draw. The motor's actual size has very little to do with that: it either provides what the fan demands or fails trying (by its protection device).
The code says, so we do, but am I missing something in the logic? Is the code requirement here simply a matter of simplicity/consistency as opposed to combating an actual safety concern?