Hello everyone,
I have been asked if a maintenance person shuts off the safety disconnect at the motor (20HP) but does not shut off the VFD disconnect, turning on the safety disconnect while the VFD is on will result in inrush current of 8 to 10 times the amp draw going through the VFD. The drives are not rated for this inrish current. The result will be damage or destruction of the drive and possibly catastrophic failure of the MCC. The VFD is located in the motor control center (MCC).The contractor suggested to install auxiliary contacts in the safety disconnects that would disable the VFD's.
Anythoughts on this ??
Thanks,
I have been asked if a maintenance person shuts off the safety disconnect at the motor (20HP) but does not shut off the VFD disconnect, turning on the safety disconnect while the VFD is on will result in inrush current of 8 to 10 times the amp draw going through the VFD. The drives are not rated for this inrish current. The result will be damage or destruction of the drive and possibly catastrophic failure of the MCC. The VFD is located in the motor control center (MCC).The contractor suggested to install auxiliary contacts in the safety disconnects that would disable the VFD's.