I understand that every VFD probably has a different response but I was looking for some typical information on what kind of current can be seen on the line side of a modern VFD during motor starting.
Are there ever VFD's that allow the full inrush current of a motor to occur or are they almost always a soft start? And for soft starting VFD's, is there a conservative assumption I can use as the (max) inrush current seen on the line side of the VFD when performing protective device coordination with upstream protective devices. This information is difficult to obtain from the vendor.
If you are looking for a specific model I have in question, I am looking at an ABB ACH550 VFD.
Are there ever VFD's that allow the full inrush current of a motor to occur or are they almost always a soft start? And for soft starting VFD's, is there a conservative assumption I can use as the (max) inrush current seen on the line side of the VFD when performing protective device coordination with upstream protective devices. This information is difficult to obtain from the vendor.
If you are looking for a specific model I have in question, I am looking at an ABB ACH550 VFD.