What should I make of this?
Recently, I found a Schneider Electric tech bulletin published in 2013 entitled "Variable Frequency Drives and Short-Circuit Current Ratings." (One may quickly find it on the web.) In it, the paper defines some basic terms such as Prospective Short-Circuit Current (PSCC), which I frequently see called available fault current (AFC). Then, the paper starts discussing the input ratings of VFDs and makes the following assertion:
The paper then provides illustration of this with some nice graphs showing peak current at about 30A for an AFC of 5kA and nearly 70A for an AFC of 100kA.
Before reading this, I would have rather expected that there was a bit more current limitation built into the input circuitry of the VFD. Also, having read previous posts in this forum regarding VFDs, I see that many here are of the opinion that modern VFDs do not so strongly affect supply harmonics, but I wonder at this if, as the paper maintains, VFD input current draw is a function of available fault current.
Is the paper correct? Or is it probable that the bulletin is focusing on older VFD designs?
If the paper is right, then there does seem to be more justification of the use of a line reactor on the infeed, not so much for harmonic mitigation of the drive, but for controlling the VFD from drawing excessive current.
I welcome the comments and discussion.
Best regards,
Shak
Recently, I found a Schneider Electric tech bulletin published in 2013 entitled "Variable Frequency Drives and Short-Circuit Current Ratings." (One may quickly find it on the web.) In it, the paper defines some basic terms such as Prospective Short-Circuit Current (PSCC), which I frequently see called available fault current (AFC). Then, the paper starts discussing the input ratings of VFDs and makes the following assertion:
The level of PSCC can have a significant thermal impact on a VFD's input diodes and capacitor bank. The VFD's input current increases significantly as the level of PSCC rises. This is caused by the input diodes conducting only when the input voltage is higher than the DC bus. The current is then limited only by the system impedance. Applying a VFD on an electrical system with a higher PSCC than the VFD input rating may cause overheating of the diodes and capacitor sections, and reduce the life expectancy of the VFD or damage the VFD.
The paper then provides illustration of this with some nice graphs showing peak current at about 30A for an AFC of 5kA and nearly 70A for an AFC of 100kA.
Before reading this, I would have rather expected that there was a bit more current limitation built into the input circuitry of the VFD. Also, having read previous posts in this forum regarding VFDs, I see that many here are of the opinion that modern VFDs do not so strongly affect supply harmonics, but I wonder at this if, as the paper maintains, VFD input current draw is a function of available fault current.
Is the paper correct? Or is it probable that the bulletin is focusing on older VFD designs?
If the paper is right, then there does seem to be more justification of the use of a line reactor on the infeed, not so much for harmonic mitigation of the drive, but for controlling the VFD from drawing excessive current.
I welcome the comments and discussion.
Best regards,
Shak