180706-2037 EDT
I read the title of this thread to mean:
We have two black box systems to compare. Both produce comparable mechanical output after startup. One black box contains a standard induction motor, started by simply closing a switch (simple starter), or possibly it includes a relay contact type of soft start. The other box contains a VFD with control means to adjust startup, and an appropriate motor for use with the VFD.
Following this assumption, then it seems to me the question is --- how do the currents from the power company or other power source to the two different black boxes compare during startup?
Alternately:
In the quote of the first post "VFDs deliver much higher frequency source power ---- " we conclude the question is about motor input current, or in the case of the VFD it is also the VFD output current.
If motor starting is primarily controlled by ramping up of a low frequency apparent approximate sine wave current frequency to the motor by short modulated current pulses of a much higher frequency, then the motor wants to follow that low frequency. Per unit time there is not much energy required to slowly accelerate the rotor and load. Thus, not a lot of input current to either the motor or the VFD input is required compared to across the line starting.
When properly modulated the high frequency current pulses to the motor are averaged or smoothed by the circuit inductance to produced an approximate low frequency sine wave. A scope plot of motor current will show a relatively smooth low frequency current waveform, not short pulses, but with some of the high frequency as ripple.
I believe the quote of the first post is wrong because a high chopping frequency of current to a motor is present whether starting or not, just different modulation, and no mention is made of the synthesized low frequency sine wave current as the primary way that starting peak current is reduced.
What I have just said may be clear as mud. So if not clear question me.
.