Do variable frequency drives cause a resonant circuit effect in the motor circuit?
To add to what the GoldMinerExcavatorDigger posted about long cables, it does happen in real life.
This is a waveform I recorded on a 660kW VSD.
It shows damped resonance but note that the horizontal time scale is in microseconds. The time frame for the fundamental motor frequency is milliseconds - three orders of magnitude different.
The waveform was measured at the motor terminal box. It's not something I like to do - exposed live terminals with the attendant risks you see.
But, as part of the contract for supplying the VSDs, we were required to demonstrate that the waveform presented to the motor was within prescribed limits for peak voltage and dv/dt.
There's a little bit of history to this and not entirely off topic in the context of the thread title, VSDs. And, hopefully, informative.
The customer, our customer, in this case had had a bad experience with another installation with three 800kW VSDs. Our customer purchased the inverters from us and the motors separately from an established motor manufacturer. The motors had a high attrition rate. About one a month. As one engineer put it at the time, an 800kW motor can't be considered a consumable item.
And, of course, the blame game started. Was the inverter or the motor to blame? Huge bucks at stake for all parties. And I lost sleep over it.
In the event, it was a baptism by fire for the motor manufacturer. They had been advised of the application but provided their standard fare which, as we later determined, just wan't up to the duty. Mesh wound and form wound will be forever etched in my brain.
It was a steep learning curve for all involved.