carlvant2004
Member
As can be seen in the pic, there is a water line above the panelboard.
Agreed, but most ECs don't pull plumbing permits.Put the waterline 'in' the joist and you are OK.
I think they are communication cables.Hard to tell from the picture but aren't the wires to close to the nailing edge? The holes for the wires in the bottom 1/3 of the joist?
These bother me more that the CVPC lines.
Yes, and it would be allowed in the dedicated space, but would not change the requirement to have no foreign systems in said space.Or use infinity's picture and install a drop ceiling.
Question??? Would one panel, above the panel, be a drop ceiling?
Violation yes but i bet inspector let it slide if you put that insulation stuf on the pipe. If going to fridge it is not likely to sweat. You do have another violation and that is the OSB board on masonry wall.
Here's a graphic from the NECH of the required dedicated space above the panel. It appears that your white pipe is within the dedicated space:
![]()