I have an outbuilding at a residence that has CSST gas piping installed in it.
The black steel pipe that ultimately connects to this is bonded at the service entrance.
The overall distance from the bond point to the CSST is about 250'
In that distance, it is black steel pipe through the house, a non metallic underground direct buried plastic pipe to the building,then at the building ,back to black steel pipe into the attic, then CSST to the heater.
How do I bond the CSST in the building?
Code as I interpret it says that it should be bonded to the electrical service grounding electrode system.
I have a 100 amp 4 wire sub feed going to the outbuildingW/ driven ground rod and #6 Cu EGC.
Is it code compliant to take the bond conductor in the outbuilding to the equipment ground bar located in the sub panel?
Even if I could get it back to the main service point and grounding electrode system, it would be at least 3 times the 75' max length allowed.
The black steel pipe that ultimately connects to this is bonded at the service entrance.
The overall distance from the bond point to the CSST is about 250'
In that distance, it is black steel pipe through the house, a non metallic underground direct buried plastic pipe to the building,then at the building ,back to black steel pipe into the attic, then CSST to the heater.
How do I bond the CSST in the building?
Code as I interpret it says that it should be bonded to the electrical service grounding electrode system.
I have a 100 amp 4 wire sub feed going to the outbuildingW/ driven ground rod and #6 Cu EGC.
Is it code compliant to take the bond conductor in the outbuilding to the equipment ground bar located in the sub panel?
Even if I could get it back to the main service point and grounding electrode system, it would be at least 3 times the 75' max length allowed.