So I installed a trough off a resi meter socket so I could add a service disconnect. In that trough I connected the neutral to trough since it was fed with PVC conduit. I received this violation:
NEUTRAL CANNOT BE CONNECTED TO TROUGH, CONNECT BOND GROUND FROM MAIN DISCONNECT.
I thought, E3609.4.1 of the MRC (IRC to those not in the mitten state) specifically requires service raceways and enclosures to be connect to the grounded (neutral) conductor if they are not connected with metal threaded connections. I'm pretty sure the NEC has a similar requirement. Am I right? Or is the inspector?
He also cited me for not using antioxidant on my aluminum feeders, which I don't think is a violation either.
NEUTRAL CANNOT BE CONNECTED TO TROUGH, CONNECT BOND GROUND FROM MAIN DISCONNECT.
I thought, E3609.4.1 of the MRC (IRC to those not in the mitten state) specifically requires service raceways and enclosures to be connect to the grounded (neutral) conductor if they are not connected with metal threaded connections. I'm pretty sure the NEC has a similar requirement. Am I right? Or is the inspector?
He also cited me for not using antioxidant on my aluminum feeders, which I don't think is a violation either.