blueheels2
Senior Member
- Location
- Raleigh, NC
- Occupation
- Electrical contractor
I built a 400 amp service. Exterior has a meter socket with a 200 amp disconnect on each side. I LB’d out of the bottom of the disconnects and pentrated the house. I set a 8”x 8”x 4’ wireway on the inside with 2 200 amp main lug panels mounted on the inside. Feeders are 4/0 Xhhw with #6 thhn as the ground. I also routed the gas bond through the trough in apiece of 1” pvc and terminated it in one of the exterior disconnects.
All raceways are pvc but the wireway is metal and needed bonding because it was isolated. In a hurry I stripped a section of the #2 cu gas bond and passed it through a lug in the wireway. My thinking was that it would be overkill, since I think I only needed to strip one of the # 6’ panel grounds to bond the wireway.
Was that a violation? Should I use one of the # 6’s instead? TIA
All raceways are pvc but the wireway is metal and needed bonding because it was isolated. In a hurry I stripped a section of the #2 cu gas bond and passed it through a lug in the wireway. My thinking was that it would be overkill, since I think I only needed to strip one of the # 6’ panel grounds to bond the wireway.
Was that a violation? Should I use one of the # 6’s instead? TIA